18th Edition Wiring Regs

Scope & Definitions

25 free practice questions with explanations

PassNova has 25 free 18th Edition Wiring Regs practice questions on Scope & Definitions, each with a clear explanation. Practise them in the browser with instant feedback — 100% free, no sign-up, on any device. Updated for 2026.

Sample questions

Scope & Definitions: example questions & answers

25 worked examples with answers and explanations below. Practise them in the browser with instant feedback on every answer.

  1. What is the primary scope of BS 7671:2018+A4:2026?

    • ADesign of electrical systems only, with installation and inspection covered separately by Building Regulations Part L
    • BRequirements for safety of persons and property from electrical hazards
    • CTesting of electrical equipment only, since design and installation rules are set out solely in the Electricity at Work Regulations 1989
    • DInstallation of renewable energy systems only, with all other mains wiring governed by BS 5839, the fire detection standard

    Answer: BS 7671 establishes the requirements for the design, installation, inspection and testing of electrical installations to protect against electrical hazards.

  2. Which of the following is NOT a voltage band defined in BS 7671?

    • AExtra low voltage (< 50V AC)
    • BUltra-high voltage (> 100kV)
    • CLow voltage (50V - 1000V AC)
    • DMedium voltage (1kV - 35kV)

    Answer: BS 7671 defines Extra Low Voltage, Low Voltage, and High Voltage bands. Ultra-high voltage is not a classification in this standard.

  3. In a TN-S earthing system, what does the 'S' represent?

    • ASeries resistance
    • BSingle phase
    • CSeparate protective conductor
    • DSupply neutral

    Answer: TN-S means the neutral and protective earth are provided by separate conductors throughout the installation.

  4. Which earthing system uses a separate earth electrode at the installation?

    • ATT
    • BIT
    • CTN-S
    • DTN-C-S

    Answer: TT (Terre-Terre) systems use a separate earth electrode at the installation, independent of the supply earth.

  5. What is the purpose of a protective conductor in an electrical installation?

    • ATo measure voltage drops
    • BTo carry the neutral current
    • CTo supply power to equipment
    • DTo provide a return path for fault current

    Answer: Protective conductors provide a return path for fault current to protect against electric shock.

  6. In BS 7671, what is defined as an accessible conductive part?

    • AAny metal part of an appliance
    • BA part buried underground
    • CAn insulated conductor
    • DA conductive part that can be touched and is not a live part

    Answer: An accessible conductive part is a conductive part that can be easily touched and is not normally a live part.

  7. Which term describes the protective conductor connecting extraneous conductive parts?

    • AMain protective conductor
    • BSupplementary bonding conductor
    • CEarth rod
    • DEquipotential bonding conductor

    Answer: Supplementary bonding conductors connect extraneous conductive parts to enhance protection against electric shock.

  8. What does the abbreviation EICR stand for?

    • AElectrical Installation Condition Report
    • BElectrical Installation Compliance Review
    • CElectrical Inspection Certification Record
    • DElectrical Installation Certificate Report

    Answer: EICR is the Electrical Installation Condition Report used for periodic inspection of existing installations.

  9. In the context of BS 7671, what is an 'extraneous conductive part'?

    • AAn external metal enclosure that forms part of the electrical equipment and is connected to the circuit protective conductor
    • BA high-voltage conductor operating above 1000V AC that is insulated from earth along its whole length
    • CA conductive part introduced from outside the installation
    • DAn earthing electrode

    Answer: An extraneous conductive part is a conductive part, not part of the electrical installation, that introduces the possibility of electric shock.

  10. What is the voltage threshold between Extra Low Voltage (ELV) and Low Voltage (LV)?

    • A30V AC
    • B50V AC
    • C40V AC
    • D60V AC

    Answer: The boundary between ELV and LV is 50V AC (or 120V DC for ELV/LV separation).

  11. Which earthing system requires an RCD for all circuits?

    • ATT
    • BTN-S
    • CTN-C-S
    • DNone of the above

    Answer: TT systems require RCD protection on all circuits because there is no metallic return path to the supply earth.

  12. In BS 7671, what does 'basic protection' refer to?

    • ASurge protection
    • BProtection against electric shock during normal operation
    • CProtection of cables from mechanical damage
    • DOvercurrent protection

    Answer: Basic protection (formerly called 'basic insulation') protects against contact with live parts during normal operation.

  13. What is a 'fault protection' measure?

    • AInsulation of conductors
    • BProtection during normal operation, provided by basic insulation and by barriers placed around live parts
    • CProtection of equipment only
    • DProtection in the event of a fault condition

    Answer: Fault protection protects against electric shock in the event of a fault, such as contact with a live part.

  14. Which of the following is an example of an IT earthing system?

    • AComputer network
    • BIndustrial three-phase system with floating neutral
    • CDomestic single-phase supply
    • DTN-S residential installation

    Answer: IT systems (Isolated or Impedance earthed) have no direct connection to earth, or through a high impedance.

  15. What is the function of a TN-C-S system's protective multiple earthing (PME)?

    • ATo reduce current flow
    • BTo eliminate neutral current by returning it through the earth electrode at each consumer's installation
    • CTo increase voltage
    • DTo provide multiple earth points along the supply cable sheath

    Answer: PME in TN-C-S systems uses multiple earth points (at pole tops, substations) to establish the reference potential.

  16. In BS 7671, what is an 'erecting person'?

    • AA person who installs equipment but takes no technical decisions, working strictly to another trade's written instructions
    • BA person responsible for design and technical decisions during installation
    • CA qualified electrician holding an NVQ Level 3, which BS 7671 requires of every person present on site
    • DA supervisor only, appointed under the Electricity at Work Regulations to sign the completion certificate

    Answer: An erecting person is someone competent to make technical decisions and direct the installation work.

  17. What defines the 'working voltage' of an electrical installation?

    • AThe actual voltage present during normal operation
    • BThe maximum voltage the cables can withstand, taken as 1000V between conductors for 6491X single-core cable
    • CThe voltage used for insulation resistance testing, which BS 7671 sets at 250V DC for a 230V circuit
    • DThe supply voltage only, taken as 240V nominal for every single-phase installation in the United Kingdom

    Answer: Working voltage is the actual voltage present in the installation during normal operation.

  18. Which standard defines 'competent person' in relation to electrical work?

    • ABS 7671 alone
    • BBS 7671 and IET guidance
    • CThe Building Regulations only
    • DBS 7909 and related standards

    Answer: BS 7671 works in conjunction with IET guidance and other standards to define competence requirements.

  19. What is the main difference between TN-C and TN-C-S systems?

    • AThe two are identical
    • BTN-C combines neutral and protective functions throughout; TN-C-S combines only up to the building
    • CTN-C requires RCDs, TN-C-S does not
    • DTN-C is used only for three-phase supplies and TN-C-S only for single-phase, so the choice follows the number of phases

    Answer: TN-C combines N and PE throughout the network; TN-C-S (PME) combines them only to the installation boundary.

  20. In BS 7671, what is meant by 'nominal voltage'?

    • AThe average voltage measured
    • BThe voltage during a fault
    • CThe maximum safe voltage
    • DThe voltage for which the installation is designed

    Answer: Nominal voltage is the voltage to which an installation is designed to operate.

  21. What is the definition of a 'circuit' in BS 7671?

    • AA cable run only
    • BA single conductor
    • CAn installation phase, meaning one of the three line conductors of a 400V supply considered on its own
    • DAn assembly of electrical equipment supplied from a single point of protection

    Answer: A circuit comprises conductors and equipment assembled to supply one or more outlets from a single protective device.

  22. Which of the following best describes 'reinforced insulation'?

    • ADouble-layer insulation with an air gap of at least 8mm maintained between the two insulating layers
    • BMetallic shielding
    • CSingle insulation layer of enhanced thickness and quality
    • DEarthed conducting layer

    Answer: Reinforced insulation is a single insulation system that provides the same level of protection as double insulation.

  23. What is the purpose of defining 'influencing factors' in BS 7671?

    • ATo measure voltage drop only, which BS 7671 limits to 6% on every final circuit whatever the load
    • BTo assess environmental and operational conditions affecting the installation
    • CTo determine cost, by fixing the price per point the designer must charge for each accessory installed
    • DTo select circuit colours, so that a borrowed neutral can be identified by brown sleeving at each accessory

    Answer: Influencing factors (external influences) must be assessed to select appropriate equipment and installation methods.

  24. In BS 7671 terminology, what is a 'final circuit'?

    • AThe supply cable
    • BThe main circuit breaker at the origin, which BS 7671 requires to be rated at 100A in all domestic premises
    • CThe earthing conductor running from the main earthing terminal to the consumer unit enclosure
    • DA circuit with outlets for connection of equipment

    Answer: A final circuit is the last circuit in a distribution system, serving outlets for equipment connection.

  25. What does 'type of earthing system' classification depend on?

    • AThe number of circuits in the installation, with more than six final circuits requiring a TT arrangement
    • BThe voltage only
    • CThe distribution network configuration and the method of earthing
    • DThe cable size only

    Answer: Earthing system type depends on how the supply is earthed and how the installation is earthed relative to the supply.

Start practising Scope & Definitions →