Earthing & Bonding
25 free practice questions with explanations
PassNova has 25 free 18th Edition Wiring Regs practice questions on Earthing & Bonding, each with a clear explanation. Practise them in the browser with instant feedback — 100% free, no sign-up, on any device. Updated for 2026.
Earthing & Bonding: example questions & answers
25 worked examples with answers and explanations below. Practise them in the browser with instant feedback on every answer.
What is a protective conductor in BS 7671 terminology?
- AAn insulated conductor carrying load current between the distribution board and a socket outlet, sized to match the line conductor
- BA conductor that provides protection against electric shock by connecting exposed parts to earth✓
- CA fuse
- DA circuit breaker only
Answer: Protective conductors (earth/ground wires) connect exposed conductive parts to the earthing system.
What is the typical color of protective conductors in UK installations?
- ABlack, which was the colour used for the neutral conductor in pre-2004 single-phase cables
- BRed
- CBlue, which identifies the neutral conductor in cables made to the harmonised colour code
- DGreen/yellow stripes✓
Answer: Protective conductors are identified by green-and-yellow striped insulation.
What is main bonding in an electrical installation?
- AConnecting components within a circuit
- BSomething UK installations do not use
- CConnecting the supply only
- DBonding main metallic services (water, gas, structural steel) to earth✓
Answer: Main bonding connects metallic services (water pipes, gas pipes, structural steel) to the earthing system.
Where should the main earth clamp be positioned on water pipes?
- AAt the water tank
- BAt any convenient location on the pipe, provided the clamp is at least 600mm from where the pipe enters
- CAt the water meter
- DWithin 600mm of the water entry to the building✓
Answer: The main earth bonding clamp on water pipes must be within 600mm of where water enters the building.
What is supplementary bonding?
- AAdditional protection beyond main bonding
- BA practice dropped from modern installations
- COnly required in TT systems
- DBonding extraneous conductive parts and exposed parts in high-risk areas (bathrooms, kitchens)✓
Answer: Supplementary bonding provides additional equipotential bonding in areas with shock risk (bathrooms, kitchens).
In a TN-S system, what is the earth electrode for?
- AReduces voltage drop
- BProvides earthing for external installations✓
- CAbsent from a TN-S system
- DUsed for lightning protection only, and it is installed by the distributor rather than by the electrician
Answer: TN-S systems may have an earth electrode for external applications, but the main earth comes from the supply neutral.
What is an earth electrode?
- AA protection device only, mounted in the consumer unit to disconnect the circuit when earth current flows
- BA type of fuse
- CA conductor or conductive object in contact with earth to establish an earth connection✓
- DAn electronic device
Answer: Earth electrodes are conductive objects (rods, plates, strips) buried in soil to establish an earth connection.
What is the typical earth electrode resistance target in TT systems?
- ALess than 50 Ohms
- BLess than 1000 Ohms
- CThe target is unspecified
- DLess than 200 Ohms✓
Answer: BS 7671 Regulation 411.5.3 requires Ra x Ia <= 50V, where Ra is the earth electrode resistance and Ia is the current that causes automatic disconnection within the required time. With a 30mA RCD this permits an earth electrode resistance of up to around 1667 Ohms in theory, but UK guidance commonly recommends a practical design target of no more than 200 Ohms, since a lower and more stable resistance is less affected by soil and weather variation and gives a more reliable installation.
How is earth electrode resistance measured?
- ABy calculation only, using the soil resistivity figure published for the local authority area
- BWith a multimeter only, set to the 200 ohm range and connected between the rod and the main earthing terminal
- CWith specialized earth loop testing equipment✓
- DA quantity that is never measured during verification
Answer: Earth electrode resistance is measured using a dedicated earth loop impedance tester.
What is an earth rod?
- AA fuse holder
- BA lightning conductor fixed to the roof ridge, which BS 7671 classes as the installation's only earth electrode
- CA cylindrical conductor (typically copper or steel) driven into the ground as an earth electrode✓
- DA circuit breaker
Answer: Earth rods are cylindrical conductors, commonly 16mm diameter and 1-3m long, driven into soil.
What is the minimum conductor size for earthing conductors in TN-S systems?
- A2.5mm²
- BHalf the main incoming cable cross-section (minimum 6mm²)✓
- C1mm²
- D16mm²
Answer: Main earthing conductors should be at least half the main cable size with a 6mm² minimum.
How should protective conductors be installed in conduit?
- AKept out of conduit altogether
- BAny way is acceptable
- CMixed with live conductors
- DSeparate from live conductors where practical✓
Answer: Protective conductors should be installed separately from live conductors to prevent thermal transfer.
What is the purpose of equipotential bonding?
- ATo reduce current
- BTo increase voltage
- CTo reduce voltage drop along the final circuit by providing a second parallel path for the load current
- DTo maintain metallic parts at similar electrical potential to prevent shock hazards✓
Answer: Equipotential bonding reduces potential differences between metallic parts, preventing shock during faults.
In bathrooms, what metallic parts typically require supplementary bonding?
- ABathtub, shower, sink taps, towel rails, and other accessible metallic parts✓
- BBonding is dispensed with
- COnly water pipes
- DOnly radiators
Answer: Bathroom bonding connects taps, radiators, towel rails, and other accessible metal to create an equipotential zone.
What is a bonding conductor?
- AOnly for main earth
- BA fuse wire
- CA conductor used to establish equipotential bonding between metallic parts✓
- DAn insulated wire
Answer: Bonding conductors connect metallic parts to reduce potential differences during fault conditions.
What color are supplementary bonding conductors?
- ABlack only
- BAny color
- CRed only
- DGreen/yellow stripes or green✓
Answer: Supplementary bonding conductors use green/yellow stripes or green insulation for identification.
How are earth rods typically driven into ground?
- ABy digging trenches at least 600mm deep and laying the rod horizontally along the bottom
- BBy hand, pushing the rod into undisturbed soil until only the connecting clamp remains above ground
- CThey are not driven at all; they are laid loose on the surface and covered with a layer of gravel
- DUsing specialized percussion driving equipment✓
Answer: Earth rods are typically driven into ground using a percussion tool to achieve proper depth and contact.
What is an earth test clamp?
- AA circuit breaker
- BA type of fuse
- CA temporary connection used during testing for safe earth loop measurements✓
- DA permanent earth connection between the main earthing terminal and the incoming water service pipe
Answer: Test clamps allow safe measurement of earth loop impedance without disconnecting the earth conductor.
In a PME (Protective Multiple Earthing) system, why are multiple earth points necessary?
- ATo limit earth conductor potential rise during fault currents✓
- BIt is simply custom, with no underlying reason
- CFor aesthetics
- DTo reduce cost
Answer: Multiple earth points in PME systems reduce the potential rise of the neutral during high fault currents.
What is the relationship between earth electrode resistance and RCD sensitivity?
- ALower electrode resistance allows lower RCD sensitivity for faster fault detection✓
- BInapplicable
- CThe two are unconnected
- DHigher resistance allows a lower RCD sensitivity, so a 500mA device may be used wherever the rod reads above 200 ohms
Answer: Lower earth electrode resistance allows use of lower RCD sensitivities (faster disconnection on faults).
How should steel gas and water pipes be bonded to earth?
- AUsing an appropriately sized bonding conductor with a labeled clamp✓
- BWith self-amalgamating tape wrapped around the pipe and the bonding conductor where they meet
- CBy direct welding of the bonding conductor to the pipe, which BS 7671 requires for all gas services
- DThey cannot be bonded, because bonding a gas pipe would create a parallel path for the supply neutral
Answer: Service pipes bond to earth using bonding conductors with labeled clamps, avoiding corrosion.
What is the maximum spacing between earth rods in a multi-rod electrode array?
- AThe rod length or greater✓
- B0.5m, measured between the centres of adjacent rods regardless of their driven depth
- CUnlimited, since rods connected in parallel behave independently of their spacing
- D1m
Answer: Multiple earth rods should be spaced at least their length apart to be effective in parallel.
In IT earthing systems, how is the neutral earthed?
- ALeft unearthed at every point, with the exposed conductive parts unearthed as well
- BThrough a resistor only, sized to hold the first earth fault current below 30mA at the point of fault
- CThrough a high impedance✓
- DDirectly to earth at the transformer star point, exactly as in a TN-S distribution system
Answer: IT systems use a high impedance (resistor or reactor) between neutral and earth.
What is the purpose of an earth loop impedance test?
- ATo test cables
- BTo measure the total impedance of the earth fault loop, verifying protection device coordination✓
- CTo measure current only, by clamping around the line conductor while the circuit carries its full design load
- DTo measure voltage only, between the line conductor and the main earthing terminal with the circuit isolated
Answer: Earth loop impedance testing verifies that protective devices will disconnect faults quickly enough.
How is protective conductor continuity verified?
- ALeft unverified
- BVisually
- CBy voltage testing
- DBy low-resistance testing (≤0.1 Ohms per connection)✓
Answer: Protective conductor continuity is verified using low-resistance measurements during initial verification.