18th Edition Wiring Regs

Earthing & Bonding

25 free practice questions with explanations

PassNova has 25 free 18th Edition Wiring Regs practice questions on Earthing & Bonding, each with a clear explanation. Practise them in the browser with instant feedback — 100% free, no sign-up, on any device. Updated for 2026.

Sample questions

Earthing & Bonding: example questions & answers

25 worked examples with answers and explanations below. Practise them in the browser with instant feedback on every answer.

  1. What is a protective conductor in BS 7671 terminology?

    • AAn insulated conductor carrying load current between the distribution board and a socket outlet, sized to match the line conductor
    • BA conductor that provides protection against electric shock by connecting exposed parts to earth
    • CA fuse
    • DA circuit breaker only

    Answer: Protective conductors (earth/ground wires) connect exposed conductive parts to the earthing system.

  2. What is the typical color of protective conductors in UK installations?

    • ABlack, which was the colour used for the neutral conductor in pre-2004 single-phase cables
    • BRed
    • CBlue, which identifies the neutral conductor in cables made to the harmonised colour code
    • DGreen/yellow stripes

    Answer: Protective conductors are identified by green-and-yellow striped insulation.

  3. What is main bonding in an electrical installation?

    • AConnecting components within a circuit
    • BSomething UK installations do not use
    • CConnecting the supply only
    • DBonding main metallic services (water, gas, structural steel) to earth

    Answer: Main bonding connects metallic services (water pipes, gas pipes, structural steel) to the earthing system.

  4. Where should the main earth clamp be positioned on water pipes?

    • AAt the water tank
    • BAt any convenient location on the pipe, provided the clamp is at least 600mm from where the pipe enters
    • CAt the water meter
    • DWithin 600mm of the water entry to the building

    Answer: The main earth bonding clamp on water pipes must be within 600mm of where water enters the building.

  5. What is supplementary bonding?

    • AAdditional protection beyond main bonding
    • BA practice dropped from modern installations
    • COnly required in TT systems
    • DBonding extraneous conductive parts and exposed parts in high-risk areas (bathrooms, kitchens)

    Answer: Supplementary bonding provides additional equipotential bonding in areas with shock risk (bathrooms, kitchens).

  6. In a TN-S system, what is the earth electrode for?

    • AReduces voltage drop
    • BProvides earthing for external installations
    • CAbsent from a TN-S system
    • DUsed for lightning protection only, and it is installed by the distributor rather than by the electrician

    Answer: TN-S systems may have an earth electrode for external applications, but the main earth comes from the supply neutral.

  7. What is an earth electrode?

    • AA protection device only, mounted in the consumer unit to disconnect the circuit when earth current flows
    • BA type of fuse
    • CA conductor or conductive object in contact with earth to establish an earth connection
    • DAn electronic device

    Answer: Earth electrodes are conductive objects (rods, plates, strips) buried in soil to establish an earth connection.

  8. What is the typical earth electrode resistance target in TT systems?

    • ALess than 50 Ohms
    • BLess than 1000 Ohms
    • CThe target is unspecified
    • DLess than 200 Ohms

    Answer: BS 7671 Regulation 411.5.3 requires Ra x Ia <= 50V, where Ra is the earth electrode resistance and Ia is the current that causes automatic disconnection within the required time. With a 30mA RCD this permits an earth electrode resistance of up to around 1667 Ohms in theory, but UK guidance commonly recommends a practical design target of no more than 200 Ohms, since a lower and more stable resistance is less affected by soil and weather variation and gives a more reliable installation.

  9. How is earth electrode resistance measured?

    • ABy calculation only, using the soil resistivity figure published for the local authority area
    • BWith a multimeter only, set to the 200 ohm range and connected between the rod and the main earthing terminal
    • CWith specialized earth loop testing equipment
    • DA quantity that is never measured during verification

    Answer: Earth electrode resistance is measured using a dedicated earth loop impedance tester.

  10. What is an earth rod?

    • AA fuse holder
    • BA lightning conductor fixed to the roof ridge, which BS 7671 classes as the installation's only earth electrode
    • CA cylindrical conductor (typically copper or steel) driven into the ground as an earth electrode
    • DA circuit breaker

    Answer: Earth rods are cylindrical conductors, commonly 16mm diameter and 1-3m long, driven into soil.

  11. What is the minimum conductor size for earthing conductors in TN-S systems?

    • A2.5mm²
    • BHalf the main incoming cable cross-section (minimum 6mm²)
    • C1mm²
    • D16mm²

    Answer: Main earthing conductors should be at least half the main cable size with a 6mm² minimum.

  12. How should protective conductors be installed in conduit?

    • AKept out of conduit altogether
    • BAny way is acceptable
    • CMixed with live conductors
    • DSeparate from live conductors where practical

    Answer: Protective conductors should be installed separately from live conductors to prevent thermal transfer.

  13. What is the purpose of equipotential bonding?

    • ATo reduce current
    • BTo increase voltage
    • CTo reduce voltage drop along the final circuit by providing a second parallel path for the load current
    • DTo maintain metallic parts at similar electrical potential to prevent shock hazards

    Answer: Equipotential bonding reduces potential differences between metallic parts, preventing shock during faults.

  14. In bathrooms, what metallic parts typically require supplementary bonding?

    • ABathtub, shower, sink taps, towel rails, and other accessible metallic parts
    • BBonding is dispensed with
    • COnly water pipes
    • DOnly radiators

    Answer: Bathroom bonding connects taps, radiators, towel rails, and other accessible metal to create an equipotential zone.

  15. What is a bonding conductor?

    • AOnly for main earth
    • BA fuse wire
    • CA conductor used to establish equipotential bonding between metallic parts
    • DAn insulated wire

    Answer: Bonding conductors connect metallic parts to reduce potential differences during fault conditions.

  16. What color are supplementary bonding conductors?

    • ABlack only
    • BAny color
    • CRed only
    • DGreen/yellow stripes or green

    Answer: Supplementary bonding conductors use green/yellow stripes or green insulation for identification.

  17. How are earth rods typically driven into ground?

    • ABy digging trenches at least 600mm deep and laying the rod horizontally along the bottom
    • BBy hand, pushing the rod into undisturbed soil until only the connecting clamp remains above ground
    • CThey are not driven at all; they are laid loose on the surface and covered with a layer of gravel
    • DUsing specialized percussion driving equipment

    Answer: Earth rods are typically driven into ground using a percussion tool to achieve proper depth and contact.

  18. What is an earth test clamp?

    • AA circuit breaker
    • BA type of fuse
    • CA temporary connection used during testing for safe earth loop measurements
    • DA permanent earth connection between the main earthing terminal and the incoming water service pipe

    Answer: Test clamps allow safe measurement of earth loop impedance without disconnecting the earth conductor.

  19. In a PME (Protective Multiple Earthing) system, why are multiple earth points necessary?

    • ATo limit earth conductor potential rise during fault currents
    • BIt is simply custom, with no underlying reason
    • CFor aesthetics
    • DTo reduce cost

    Answer: Multiple earth points in PME systems reduce the potential rise of the neutral during high fault currents.

  20. What is the relationship between earth electrode resistance and RCD sensitivity?

    • ALower electrode resistance allows lower RCD sensitivity for faster fault detection
    • BInapplicable
    • CThe two are unconnected
    • DHigher resistance allows a lower RCD sensitivity, so a 500mA device may be used wherever the rod reads above 200 ohms

    Answer: Lower earth electrode resistance allows use of lower RCD sensitivities (faster disconnection on faults).

  21. How should steel gas and water pipes be bonded to earth?

    • AUsing an appropriately sized bonding conductor with a labeled clamp
    • BWith self-amalgamating tape wrapped around the pipe and the bonding conductor where they meet
    • CBy direct welding of the bonding conductor to the pipe, which BS 7671 requires for all gas services
    • DThey cannot be bonded, because bonding a gas pipe would create a parallel path for the supply neutral

    Answer: Service pipes bond to earth using bonding conductors with labeled clamps, avoiding corrosion.

  22. What is the maximum spacing between earth rods in a multi-rod electrode array?

    • AThe rod length or greater
    • B0.5m, measured between the centres of adjacent rods regardless of their driven depth
    • CUnlimited, since rods connected in parallel behave independently of their spacing
    • D1m

    Answer: Multiple earth rods should be spaced at least their length apart to be effective in parallel.

  23. In IT earthing systems, how is the neutral earthed?

    • ALeft unearthed at every point, with the exposed conductive parts unearthed as well
    • BThrough a resistor only, sized to hold the first earth fault current below 30mA at the point of fault
    • CThrough a high impedance
    • DDirectly to earth at the transformer star point, exactly as in a TN-S distribution system

    Answer: IT systems use a high impedance (resistor or reactor) between neutral and earth.

  24. What is the purpose of an earth loop impedance test?

    • ATo test cables
    • BTo measure the total impedance of the earth fault loop, verifying protection device coordination
    • CTo measure current only, by clamping around the line conductor while the circuit carries its full design load
    • DTo measure voltage only, between the line conductor and the main earthing terminal with the circuit isolated

    Answer: Earth loop impedance testing verifies that protective devices will disconnect faults quickly enough.

  25. How is protective conductor continuity verified?

    • ALeft unverified
    • BVisually
    • CBy voltage testing
    • DBy low-resistance testing (≤0.1 Ohms per connection)

    Answer: Protective conductor continuity is verified using low-resistance measurements during initial verification.

Start practising Earthing & Bonding →