Inspection & Testing
25 free practice questions with explanations
PassNova has 25 free 18th Edition Wiring Regs practice questions on Inspection & Testing, each with a clear explanation. Practise them in the browser with instant feedback — 100% free, no sign-up, on any device. Updated for 2026.
Inspection & Testing: example questions & answers
12 worked examples with answers and explanations below. Practise all 25 Inspection & Testing questions free in the browser, with instant feedback on every answer.
What is initial verification in electrical installations?
- AMonthly checking
- BThe complete inspection and testing of a new installation before it is put into service✓
- CAnnual maintenance
- DNever required
Answer: Initial verification is the comprehensive testing required before an installation is energized.
What is an EICR (Electrical Installation Condition Report)?
- AA design document
- BThe report produced during periodic inspection of existing installations✓
- CA maintenance schedule
- DA warranty document
Answer: An EICR documents the condition of an existing electrical installation and identifies defects.
What is the typical interval for periodic inspection of a domestic installation?
- A1 year
- B3 years
- C10 years
- DEvery 5-10 years or on change of occupancy✓
Answer: BS 7671 recommends periodic inspection every 10 years for domestic installations, or on change of occupancy.
What is an EIC (Electrical Installation Certificate)?
- AA testing tool
- BA certificate confirming a new installation meets BS 7671✓
- CAn insurance document
- DA maintenance log
Answer: An EIC is the certification provided after successful initial verification of a new installation.
What is the main purpose of visual inspection before electrical testing?
- AAesthetic check only
- BTo identify visible damage, defects, and compliance issues before energizing✓
- CTo ensure good color matching
- DNo purpose
Answer: Visual inspection checks for physical damage, incorrect installation, and non-compliant work before testing.
Which test should be performed first on a new installation?
- AInsulation resistance
- BEarth continuity
- CVisual inspection✓
- DLoading test
Answer: Visual inspection must be completed before any testing to ensure it is safe to energize.
What is insulation resistance testing?
- ATesting cable outer cover strength
- BMeasuring the resistance between conductors and earth to verify insulation integrity✓
- CTesting circuit breaker operation
- DChecking conductor size
Answer: Insulation resistance testing uses a megohmmeter to verify insulation between conductors and earth.
What is the minimum acceptable insulation resistance for a 230V installation?
- A0.5 MΩ
- B1 MΩ✓
- C5 MΩ
- D10 MΩ
Answer: BS 7671 specifies minimum 1 MΩ insulation resistance at 500V DC test voltage.
What is the test voltage for insulation resistance on a 230V installation?
- A110V DC
- B230V DC
- C500V DC✓
- D1000V DC
Answer: Insulation resistance testing on low-voltage installations uses 500V DC as the test voltage.
What is protective conductor continuity testing?
- ATesting cable insulation
- BMeasuring the resistance of earth and bonding conductors to ensure low-resistance paths✓
- CTesting circuit breaker function
- DChecking voltage
Answer: Protective conductor continuity testing measures resistance of earth paths to verify they are adequate.
What is the maximum acceptable resistance for a protective conductor?
- A10 Ohms
- B1 Ohm
- C0.1 Ohms per connection, typically✓
- D100 Ohms
Answer: Protective conductor resistance should be very low, typically ≤0.1 Ohms at each joint.
What is earth fault loop impedance (Zs) testing?
- ATesting insulation
- BMeasuring the impedance of the complete fault current path to verify protection coordination✓
- CTesting voltage stability
- DCable capacity testing
Answer: Zs testing measures the impedance from the transformer secondary to the fault point, verifying overcurrent protection.