  1. What is initial verification in electrical installations?

    • AMonthly checking
    • BThe complete inspection and testing of a new installation before it is put into service
    • CAnnual maintenance
    • DNever required

    Answer: Initial verification is the comprehensive testing required before an installation is energized.

  2. What is an EICR (Electrical Installation Condition Report)?

    • AA design document
    • BThe report produced during periodic inspection of existing installations
    • CA maintenance schedule
    • DA warranty document

    Answer: An EICR documents the condition of an existing electrical installation and identifies defects.

  3. What is the typical interval for periodic inspection of a domestic installation?

    • A1 year
    • B3 years
    • C10 years
    • DEvery 5-10 years or on change of occupancy

    Answer: BS 7671 recommends periodic inspection every 10 years for domestic installations, or on change of occupancy.

  4. What is an EIC (Electrical Installation Certificate)?

    • AA testing tool
    • BA certificate confirming a new installation meets BS 7671
    • CAn insurance document
    • DA maintenance log

    Answer: An EIC is the certification provided after successful initial verification of a new installation.

  5. What is the main purpose of visual inspection before electrical testing?

    • AAesthetic check only
    • BTo identify visible damage, defects, and compliance issues before energizing
    • CTo ensure good color matching
    • DNo purpose

    Answer: Visual inspection checks for physical damage, incorrect installation, and non-compliant work before testing.

  6. Which test should be performed first on a new installation?

    • AInsulation resistance
    • BEarth continuity
    • CVisual inspection
    • DLoading test

    Answer: Visual inspection must be completed before any testing to ensure it is safe to energize.

  7. What is insulation resistance testing?

    • ATesting cable outer cover strength
    • BMeasuring the resistance between conductors and earth to verify insulation integrity
    • CTesting circuit breaker operation
    • DChecking conductor size

    Answer: Insulation resistance testing uses a megohmmeter to verify insulation between conductors and earth.

  8. What is the minimum acceptable insulation resistance for a 230V installation?

    • A0.5 MΩ
    • B1 MΩ
    • C5 MΩ
    • D10 MΩ

    Answer: BS 7671 specifies minimum 1 MΩ insulation resistance at 500V DC test voltage.

  9. What is the test voltage for insulation resistance on a 230V installation?

    • A110V DC
    • B230V DC
    • C500V DC
    • D1000V DC

    Answer: Insulation resistance testing on low-voltage installations uses 500V DC as the test voltage.

  10. What is protective conductor continuity testing?

    • ATesting cable insulation
    • BMeasuring the resistance of earth and bonding conductors to ensure low-resistance paths
    • CTesting circuit breaker function
    • DChecking voltage

    Answer: Protective conductor continuity testing measures resistance of earth paths to verify they are adequate.

  11. What is the maximum acceptable resistance for a protective conductor?

    • A10 Ohms
    • B1 Ohm
    • C0.1 Ohms per connection, typically
    • D100 Ohms

    Answer: Protective conductor resistance should be very low, typically ≤0.1 Ohms at each joint.

  12. What is earth fault loop impedance (Zs) testing?

    • ATesting insulation
    • BMeasuring the impedance of the complete fault current path to verify protection coordination
    • CTesting voltage stability
    • DCable capacity testing

    Answer: Zs testing measures the impedance from the transformer secondary to the fault point, verifying overcurrent protection.