Inspection & Testing
28 free practice questions with explanations
PassNova has 28 free 18th Edition Wiring Regs practice questions on Inspection & Testing, each with a clear explanation. Practise them in the browser with instant feedback — 100% free, no sign-up, on any device. Updated for 2026.
Inspection & Testing: example questions & answers
28 worked examples with answers and explanations below. Practise them in the browser with instant feedback on every answer.
What is initial verification in electrical installations?
- AMonthly checking of the consumer unit by the occupier, recorded in a log kept on the premises
- BThe complete inspection and testing of a new installation before it is put into service✓
- CAnnual maintenance carried out on an existing installation and recorded on a Minor Works Certificate
- DA step that is never required at any stage before a new installation is put into service
Answer: Initial verification is the comprehensive testing required before an installation is energized.
What is an EICR (Electrical Installation Condition Report)?
- AA maintenance schedule setting out the tasks to be carried out on the installation each year
- BA design document
- CA warranty document issued by the maker of the consumer unit and valid for six years from purchase
- DThe report produced during periodic inspection of existing installations✓
Answer: An EICR documents the condition of an existing electrical installation and identifies defects.
What is the typical interval for periodic inspection of a domestic installation?
- AEvery 5-10 years or on change of occupancy✓
- B1 year
- C3 years, halved to 18 months where the property has an off-peak storage heating circuit
- D10 years from the date the property was built, after which no further inspection is needed
Answer: BS 7671 recommends periodic inspection every 10 years for domestic installations, or on change of occupancy.
What is an EIC (Electrical Installation Certificate)?
- AA certificate confirming a new installation meets BS 7671✓
- BA maintenance log recording each visit made to the installation after it was first energised
- CA testing tool
- DAn insurance document transferring liability for the installation from the installer to the insurer
Answer: An EIC is the certification provided after successful initial verification of a new installation.
What is the main purpose of visual inspection before electrical testing?
- ATo ensure good colour matching between the accessories and the decoration of the room
- BIt serves no purpose, as BS 7671 treats visual inspection as optional once dead testing is complete
- CAn aesthetic check only, confirming faceplates are level and their screws aligned vertically
- DTo identify visible damage, defects, and compliance issues before energizing✓
Answer: Visual inspection checks for physical damage, incorrect installation, and non-compliant work before testing.
Which test should be performed first on a new installation?
- AVisual inspection✓
- BLoading test
- CInsulation resistance
- DEarth continuity
Answer: Visual inspection must be completed before any testing to ensure it is safe to energize.
What is insulation resistance testing?
- ATesting circuit breaker operation
- BChecking conductor size
- CTesting cable outer cover strength
- DMeasuring the resistance between conductors and earth to verify insulation integrity✓
Answer: Insulation resistance testing uses a megohmmeter to verify insulation between conductors and earth.
What is the minimum acceptable insulation resistance for a 230V installation?
- A1 MΩ✓
- B0.5 MΩ
- C10 MΩ
- D5 MΩ
Answer: BS 7671 specifies minimum 1 MΩ insulation resistance at 500V DC test voltage.
What is the test voltage for insulation resistance on a 230V installation?
- A1000V DC
- B110V DC
- C230V DC
- D500V DC✓
Answer: Insulation resistance testing on low-voltage installations uses 500V DC as the test voltage.
What is protective conductor continuity testing?
- ATesting circuit breaker function
- BMeasuring the resistance of earth and bonding conductors to ensure low-resistance paths✓
- CChecking voltage
- DTesting cable insulation
Answer: Protective conductor continuity testing measures resistance of earth paths to verify they are adequate.
What is the maximum acceptable resistance for a protective conductor?
- A1 Ohm
- B10 Ohms
- C0.1 Ohms per connection, typically✓
- D100 Ohms, the same limit that applies to an earth electrode in a TT installation
Answer: Protective conductor resistance should be very low, typically ≤0.1 Ohms at each joint.
What is earth fault loop impedance (Zs) testing?
- ACable capacity testing
- BTesting voltage stability at the origin over a 24-hour period to confirm the supply stays within tolerance
- CMeasuring the impedance of the complete fault current path to verify protection coordination✓
- DTesting insulation
Answer: Zs testing measures the impedance from the transformer secondary to the fault point, verifying overcurrent protection.
What is prospective fault current (PFC) testing?
- ACalculating the maximum possible fault current at a point to verify equipment ratings✓
- BTesting switch ratings by operating each switch a hundred times at its full rated load current
- CA test that is not carried out
- DTesting cables only, by passing twice the design current through each conductor for one whole minute
Answer: PFC is calculated to ensure switchgear and protective devices are rated for the potential fault current.
What is the purpose of an RCD functional test?
- ATo verify that RCDs trip at their rated sensitivity✓
- BTo test circuit breaker operation by measuring the time taken to reset the device after it trips
- CUnnecessary, since the manufacturer's factory test certificate covers the device for its whole life
- DTo measure voltage only, between the load terminals of the device and the main earthing terminal
Answer: RCD functional testing (typically using a test button) verifies the device operates correctly.
What testing equipment is essential for initial verification?
- AMultimeter only
- BThe certificate may be completed from the design calculations, so no instruments are needed
- CMultimeter, insulation tester, earth loop tester, and phase rotation meter✓
- DVoltmeter only
Answer: Initial verification requires an insulation tester (megohmmeter), earth loop tester, and other specialized equipment.
What is the schedule of test results (SOR)?
- AA maintenance plan
- BA document recording all test data from initial verification✓
- CA project timeline
- DA list of the equipment purchased for the job, with prices and the supplier's delivery note numbers
Answer: The Schedule of Test Results documents all electrical testing measurements and results.
What must be checked during visual inspection regarding cable routing?
- ATemperature only, measured with an infrared thermometer at each accessory while the circuit is loaded
- BProper support, protection from mechanical damage, and appropriate installation methods✓
- COnly colour coding, checking the sheath colour matches the circuit chart on the distribution board
- DCable routing is checked during dead testing rather than during the visual inspection stage
Answer: Visual inspection checks cable support, protection methods, and compliance with routing standards.
What is the purpose of labeling verification during inspection?
- ATo check that the colour of each printed label matches the colour of the accessory it is fixed to
- BAesthetic only, ensuring labels are printed in the same typeface throughout the installation
- CUnimportant, because circuit identification is recorded on the certificate rather than at the board
- DTo ensure circuits are identified and protective devices are correctly rated and labeled✓
Answer: Labeling verification confirms all circuits are identified and protective devices are properly marked.
What is a minor works certificate (MWC)?
- AA certificate for work not requiring full EIC (e.g., single circuit modifications)✓
- BA maintenance log kept on site recording every alteration made to the installation since handover
- CAn insurance document confirming the installer holds public liability cover for the work done
- DA document unknown in the UK, since minor works are certified on a full EIC like any other job
Answer: An MWC certifies minor electrical work that doesn't require a full electrical installation certificate.
What testing is required for supplementary bonding verification?
- ALow-resistance continuity testing of bonding conductors✓
- BVoltage testing only, between each bonded part and the main earthing terminal with the supply on
- CContinuity testing of the bonding conductors is not carried out
- DInsulation resistance only, applied at 500V DC between the bonding conductor and the metalwork
Answer: Supplementary bonding is verified using continuity testing to measure resistance between bonded parts.
What is the purpose of initial verification's dead testing?
- AA stage that is skipped, since insulation and continuity are checked as the work proceeds
- BTesting with power OFF to verify insulation, continuity, and component correctness✓
- CEmergency shutdown testing, operating the fireman's switch to confirm it isolates the whole installation
- DTesting circuits when powered, so the true operating temperature of each conductor can be measured
Answer: Dead testing is performed with the supply OFF to safely verify insulation and continuity.
What is the sequence of live testing in initial verification?
- ALive testing is not required
- BAny order is acceptable
- CPhase rotation, voltage, RCD test, then load testing in a controlled sequence✓
- DA sequence that BS 7671 does not define
Answer: Live testing follows a controlled sequence starting with phase rotation and voltage verification.
What is the purpose of RCD trip-time testing with sine-wave current?
- ATo verify RCD operates within specified time limits at its rated current✓
- BTo measure voltage only, checking that the supply stays above 207V while the device is being tested
- CDispensed with, as the trip time is fixed by the device's design and cannot drift
- DTo test circuit breaker operation, confirming the magnetic element trips within 0.1 seconds at five times its rating
Answer: RCD trip-time testing verifies that RCDs disconnect within specified time (typically 300ms at 5×In).
Which of these is NOT one of the tests required by BS 7671 for the initial verification of an installation?
- AContinuity of the protective conductors
- BInsulation resistance between live conductors and earth
- COperating each circuit at its rated load to measure the temperature rise✓
- DEarth fault loop impedance measured at the furthest point of each circuit
Answer: Regulation 643 sets out the tests for initial verification: continuity of protective conductors and of ring final circuit conductors, insulation resistance, polarity, earth electrode resistance where one is used, earth fault loop impedance, RCD operation, phase sequence and functional testing, together with verification of voltage drop. Loading a circuit to its rated current to measure temperature rise is a type test done by equipment manufacturers, not part of verifying an installation.
What information must an EIC contain?
- AJust test dates
- BOnly equipment serial numbers, with the date each item was delivered to site by the wholesaler
- CDesigner, installer, inspector details; test results; description of work; and declaration of compliance✓
- DOnly a circuit list, since test values are recorded separately and are never issued to the person ordering the work
Answer: An EIC includes designer/installer/inspector information, descriptions of work, test results, and compliance declaration.
During initial verification of a ring final circuit, r1, rn and r2 are each measured end-to-end, the line and cpc conductors are then cross-connected at the distribution board, and resistance is measured at every outlet. What does this test confirm?
- AThe insulation resistance between the line and neutral conductors, which BS 7671 requires to be at least 1 megohm when measured at 500V DC with the ring's cross-connections still in place at the board
- BThe polarity of the main switch only
- CThe voltage drop across the installation under full load
- DThat the ring is continuous with no breaks, and that every outlet is correctly wired into the ring rather than incorrectly spurred or cross-connected✓
Answer: The end-to-end readings (r1 for line, rn for neutral, r2 for cpc) confirm each conductor loops all the way round the ring without a break. Cross-connecting line and cpc at the board and measuring at each outlet should then give a broadly consistent reading, approximately (r1+r2)/4, at every socket - confirming the ring is wired as a true continuous loop, with no breaks, interconnections, or outlets wrongly wired as a spur from only one leg.
What is the main purpose of polarity testing during the initial verification of an installation?
- ATo confirm that single-pole switching and protective devices are connected in the line conductor only, and that connections at accessories (such as an Edison screw lampholder's centre contact) follow the correct polarity✓
- BTo confirm that an RCD trips within its required disconnection time
- CTo check that cable core colours match the manufacturer's catalogue photographs
- DTo measure the earth fault loop impedance at the furthest point on the circuit
Answer: Polarity testing confirms that single-pole devices (switches, protective devices) are wired into the line conductor rather than the neutral. If a switch were wired into the neutral instead, the accessory would appear switched off while the line conductor - and the equipment beyond it - remained live, creating a shock risk. It also confirms correct polarity at accessories, such as the centre contact of an Edison screw lampholder being connected to line rather than neutral.
A single-pole light switch has been wired into the neutral conductor instead of the line conductor. What is the safety consequence, and which test during initial verification is designed to catch this fault before the installation is put into service?
- AThe switch still interrupts current flow to the lamp when operated, so the installation stays safe
- BThe lamp holder and its wiring remain live even when the switch is off, which is exactly the fault that polarity testing is designed to catch✓
- CThe circuit's RCD will trip immediately, so no specific test is needed to detect the fault
- DThe lamp will simply fail to light at all, making the fault obvious without any specific test being required, so it is picked up during the functional check at the end of the job rather than by any measurement taken during initial verification
Answer: Switching in the neutral conductor leaves the line conductor - and therefore the lamp holder and its downstream wiring - live even when the switch is off, creating a serious shock risk for anyone changing a lamp or accessing the fitting. The circuit still switches the lamp on and off normally in use, so the fault isn't obvious without testing. This is exactly why polarity testing is a mandatory, dedicated part of initial verification.